Honeywell T7351 Thermostat User Manual


 
T7351 COMMERCIAL PROGRAMMABLE THERMOSTAT
9 63-2666—02
OATSENS 0 0 - 1 Outdoor Air Sensor Selection
0: None
1: Remote Outdoor Air Sensor
DATSENS 0 0 - 1 Discharge Air Sensor Selection
0: None
1: Remote Discharge Air Sensor
HUMSENS 0 0 - 2 Room Humidity Sensor selection
0: None
1: On Board Sensor
2: Remote Sensor
OCCSENS 0 0 - 1 Occupancy Sensor Selection
0: None
1: Remote Occ Sensor
FAN HT 0 0 - 1 Fan Operation on Heat
0: Conventional (Equipment controls Fan)
1: Electric (Thermostat turns on Fan with call for Heat)
XFAN HT YES YES or NO Extended Fan on Heat
NO: None
YES: 90 seconds
XFAN CL NO YES or NO Extended Fan on Cool
NO: None
YES: 40 seconds
STRTDEL 0 0 - 15 Sequential Start Delay
0 to 150 seconds in 10 second increments
ADVANCE NO YES or NO Advanced Settings
NO: Hide
YES: Show
TMP LIM 3 0 - 5 Temporary Setpoint Adjustment
0: 0 Deg. F
1: 1 Deg. F
2: 2 Deg. F
3: 3 Deg. F
4: 4 Deg. F
5: 5 Deg. F
TMP OCC 3 1 - 8 Temporary Occupied Duration
1 to 8 hours
TMP CAL 0 -4 - 3 Temporary Display Adjustment
0 - 3 = 0 to 3 DDF
4 - 7 = -4 to -1 DDF
MINCOOL 45° F
(7° C)
45° - 99° F
(7° - 37° C)
Min Cool Setpoint
MAXHEAT 90° F
(32° C)
40° - 90° F
(4° - 32° C)
Max Heat Setpoint
HEATLCK NO YES or NO Heating Lockout (Only displayed if Outdoor Air Sensor is selected)
NO: None
YES: Enabled
HTLCKSP 70° F
(21° C)
-40° - 120 ° F
(-40° - 49° C)
Heating Lockout Temperature
(Display only if Remote Outdoor Air Sensor is configured)
COOLLCK NO YES or NO Cooling Lockout (Only displayed if Outdoor Air Sensor is Selected)
NO: None
YES: Enabled
CLLCKSP 35° F
(2° C)
-40° - 120° F
(-40° - 49° C)
Cooling Lockout Temperature
(Display only if Remote Outdoor Air Sensor is configured)
DAT LL NO YES or NO Discharge Low Limit (Only displayed if Discharge Air Sensor is Selected)
NO: None
YES: Enabled
DATLLSP 45° F
(7° C)
35° - 60° F
(2° - 16° C)
Discharge Low Temp Limit
(Display only if Discharge Sensor is configured)
Table 5. Installer Setup. (Continued)
Text Default Choices Notes