41 63-4368
Table 21. T7350H Network Variable Summary. (Continued)
Nv Name L
ONSPEC™ Ref Name Class Description
nvoOccSchedule Time Of Day Out OUT This output has current state, next state and tuncos (Time Until
Change of State). This output is typically bound to other
controller(s) that need a schedule command.
This output is the combination of the local schedule and the
network schedule command. It doesn’t include any bypass,
override, or manual occupancy commands that affect this T7350H.
There is no TOD assignment table in the T7350H. The T7350H
allows a one to many binding of nvoOccSchedule. This means
one T7350H can command all of the XL10s on the subnet – up to
119 controllers.
Current scheduled occupancy state:
0: OC_OCCUPIED
1: OC_UNOCCUPIED
3: OC_STANDBY
-1: OC_NUL (power up value).
Next scheduled occupancy state:
0: OC_OCCUPIED (power up value).
1: OC_UNOCCUPIED
3: OC_STANDBY
-1: OC_NUL (power up value).
Time in minutes until next scheduled change of occupancy state:
2880: Means there is not a next change of occupancy state or it is
longer than 2 days from now (Power up value).
nvoOccSensor Occupancy Sensor Out OUT Status of occupancy sensor:
0: OC_OCCUPIED
1: OC_UNOCCUPIED
-1: OC_NUL (not configured and power up value).
nvoOutdoorTemp Outdoor Temperature Out OUT The current outdoor temperature (Celsius). The sensor source is
specified by nciConfig.oDAirSensor. A value of 327.67 means the
sensor is not functioning correctly or is out of range.
327.67: Power up value.
nvoPgm Program Out OUT Cover assembly flash memory programming data.
nvoSpaceRH Space Humidity Out OUT The current space humidity (percent). The sensor source is
specified by nciConfig.humiditySensor. A value of 163.84 means
the sensor is not functioning correctly or is out of range.
163.84: Power up value.
nvoSpaceTemp Space Temperature Out OUT The current space temperature (Celsius). The sensor source is
specified by nciConfig.spaceSensor. A value 327.67 means the
sensor is not functioning correctly or is out of range.
327.67: power up value.