T7350 COMMERCIAL PROGRAMMABLE THERMOSTAT
63-4368 40
Table 21. T7350H Network Variable Summary. (Continued)
Nv Name L
ONSPEC™ Ref Name Class Description
nvoBypass Bypass Out OUT The T7350H uses nvoBypass to command bypass to other XL10
nodes. When the T7350 is in bypass, it commands nvoBypass.
This is a one to many bound relationship. “Many” means one
T7350H can command bypass on all XL10s connected on the
subnet.
Reports whether this device is in timed bypass of the scheduled
occupancy state. Used by other devices to also bypass the time of
day schedule.
Value
State Action
0 0 This device is not in bypass
Power up value
1 100 This device is in bypass
nvoData1 nvoData1 OUT Reports Manufacturer Specific Device Data including:
bypassTime, coolStgsOn, DaysLeftKeypadHoliday, dischTemp,
effMode, effOccCurrentState, effSetPt, fan, heatStgsOn, oDTemp,
percentCmd,Cool, percentCmdHeat, spaceHumidity, spaceTemp,
subBaseType, sysMode, terminalLoad.
nvoData2 nvoData2 OUT Reports Manufacturer Specific Device Data including: auxRelay,
DALimit, dehumidActive, ESR, holiday, noAuxHeat1, noAuxHeat2,
occSensor, relayAux, relayCool1, relayCool2, relayCool3,
relayFan, relayHeat1, relayHeat2, relayHeat3, remoteStPtOffset,
schedNextState, scheduledState, scheduledTuncos, stagesActive,
T7350CommWorks, temporarySetPt, totalError.
nvoDischAirTemp Discharge Temperature
Out
OUT The current discharge air temperature (Celsius). The sensor is
configured by nciConfig.dischAirSensor. A value of 327.67 means
the sensor is not functioning correctly or is out of range.
327.67: Power up value.
nvoEffectOccup Effective Occ Out OUT Current effective occupancy state:
0: OC_OCCUPIED (power up value).
1: OC_UNOCCUPIED
2: OC_BYPASS
3: OC_STANDBY
-1: OC_NUL
nvoEffectSetpt Effective Stpt Out OUT Effective room temperature control set point (Celsius).
327.67: Power up value.
nvoError nvoError OUT Device error status. Refer to Appendix C - Network Error
Reporting for details.
nvoFileStat File Status Out OUT File transfer status.
nvoHeatCool Application Mode out OUT Effective operating mode:
0: HVAC_AUTO
1: HVAC_HEAT (heat or re-heat).
3: HVAC_COOL
6: HVAC_OFF (power up value).
7: HVAC_TEST (manual mode or cover in factory test mode).
8: HVAC_EMERG_HEAT