Heatiator T4800 Indoor Fireplace User Manual


 
34922 Rev B 10 12-01
T4800 INSTALLATION INSTRUCTIONS
Figure 5 - Framing the Fireplace
WARNING!
Do not apply combustible finishing materials over any part of the black face of this fireplace or a structure
fire may result. The black metal fireplace front may only be covered with noncombustible materials such
as ceramic tile, brick, or stone. Do not cover or block any cooling air slots. Do not cover any portion of the
opening to the fireplace that would prevent the installation of an authorized glass door.
Figure 6 - Sidewalls and Surrounds
2. Framing the Fireplace
The T4800 fireplace will fit a framed opening of 56
7
/8 wide x 49
3
/8 tall. The finished cavity depth must be no less
than 30
5
/8.
Figure 5 shows a typical framing (using 2 x 4 lumber) of the fireplace, assuming combustible materials are used.
All required clearances to combustibles around the fireplace must be adhered to. Any framing across the top of the
fireplace must be above the level of the top standoffs. Chimney sections at any level require a 2 minimum air
space clearance between the framing and chimney section.
3. Sidewalls/Surrounds
Adjacent combustible side walls must be located a minimum of 24 from the fireplace opening. See Figure 6. If you
are using a decorative surround constructed of combustible material, it must be located within the shaded area
defined in Figure 6. Short stub walls are also acceptable if they are contained within the shaded area.
CLEARANCES!
A minimum 1½ air clearance
must be maintained at the
back and sides of the
fireplace assembly except at
the nailing flange where the
clearance is ½.
Chimney sections at any level
require a 2 minimum air
space clearance between the
framing and chimney section.